4 types of shallow geothermal
1-2m horizontal collectors (“gound heat collectors”)
4-50m groundwater wells
40-250m borehole heat exchanger
40-250m borrhole heat exchanger fields
what is the Carnot Number εc ?
maximum possible output 𝑄𝐻 of a heat pump with electrical or mechanical
power 𝑃𝑝 theoretical optimum
Ec = Th / (Th- Tc)
Pp= Qh / Ec = 1 / Ec
What are the 9 types of Usage of Shallow
Geothermal Energy?
borehole heat exchanger
BHE field
thermal use of spring water
thermal use of funnel
horizontal collectors
pile heat exchanger
surface water use
groundwater heat pump
trench collector
waste water usage
Which shallow geothermal systems are open and which ones are closed systems?
open system:
ground water heat pump
closed systems:
BHE
geothermal heat collector
energy pile
What´s the difference between
performance number ε (Leistungszahl)
COP
SCOP
?
performance number ε does not take into account other needed electric power like the heat circulation pump or a water pump
COP involves also other electric processes like the heat circulation pump or a water pump
𝐶𝑂𝑃=𝑄𝑊/𝑃𝑊𝑒𝑙
ratio between the released heat energy under changing operation conditions and the used operating power in aspecific time intervall
𝛽𝑎=𝑄ℎ / 𝑊𝑒𝑙
The geothermal productivity is based on ? 5 points
soil characteristics
local climate
thermic regeneration in summer
laying depth
minimal operating temperature
Why is the modelling of Shallow Horizontal Collectors (SHC) a challanging task?
due to its complicated geometry
due to the co-existence of different heat transport mechanisms (advection (advection = vertical convection) in the pipes and conduction in the ground)
different driving forces (thermal load, air temperature and its dampening at different depths below the ground surface, time varying water saturation etc.).
For these reasons, rule of thumb sizing tables are adopted
How to calculate the maximum specific heat abstraction capacity of a ground heat collector?
q [W/m²] = Q[W] / A [m²]
Q[W]= q [W/m²] x A [m²]
What are the specifics and advantages of D
irect heat exchanger ?
the cooling agent of the heat pump) flows directly in the pipes of the
ground heat collector
lower efforts to build up
higher SCOP
higher amount of cooling agent
seamless pipes needed
higher costs for copper ) pipes
higher distances between the piles because
Energy piles are …
EP use…
In order to use EP we need …
EP are closed systems with thermal recovery.
EP use construction components (concrete piles or slabs).
In order to use EP we need…
IF no or low groundwater flux through:
active thermal regeneration.
heat extraction heating ): 25 30 W/ m pile , 50 80 kWh/( a∙m pile
heat supply cooling ): max. of 30 W/ m pile , 20 60 kWh/( a∙m pile
IF high groundwater flux
low seasonal depency between